FR-CS80 - PU + EXT control and Term.4 Analog Input
Objective:
Configure a VSD to allow for PU and EXT Analog Speed reference control.
Step-by-Step Procedure for Configuring FR-CS80 VSD for PU and EXT Analog Speed Reference Control
Prerequisites
-
Hardware :
- Mitsubishi FR-CS80 VSD (e.g., FR-CS80-025-60 for a 0.75 kW motor).
- Potentiometer (10 kΩ recommended for 0–10 V control) or analog signal source (e.g., 4–20 mA from a PLC).
- Wiring tools, shielded cables for analog signals, and terminal connectors.
- PC with FR Configurator2 software (optional, for parameter backup or monitoring).
-
Documentation :
- FR-CS80 Instruction Manual (IB(NA)-0600639ENG). (or better yet… the latest updated eManual Viewer)
- Motor nameplate data (voltage, current, frequency).
-
Safety :
- Ensure the VSD and motor are powered off during wiring.
- Verify proper grounding of the VSD and motor to prevent electrical hazards.
Step-by-Step Procedure
Step 1: Wiring the FR-CS80 VSD
- Power Off and Verify :
- Disconnect power to the VSD and motor.
- Wait 5 minutes for the VSD’s internal capacitors to discharge (check the charge indicator LED is off).
- Connect the Motor :
- Wire the motor to the VSD’s output terminals (U, V, W) using appropriately sized cables based on motor current.
- Ensure correct phase sequence (U→U, V→V, W→W) to avoid reverse rotation.
- Connect the motor’s ground wire to the VSD’s ground terminal (PE).
- Connect Power Supply :
- Wire the three-phase power supply (e.g., 200–240 V for FR-CS80-025-60) to the VSD’s input terminals (R/L1, S/L2, T/L3).
- Connect the ground wire to the PE terminal.
- Wire the Potentiometer for EXT Analog Speed Reference :
- Use a 10 kΩ potentiometer for 0–10 V control (recommended for simplicity).
- Connect the potentiometer’s three terminals to the VSD’s control terminals:
- Positive (+) : Connect one outer terminal to terminal 10 (provides +5 V or +10 V, depending on Pr. 73 setting).
- Wiper (center) : Connect to terminal 2 (analog voltage input, 0–10 V).
- Negative (−) : Connect the other outer terminal to terminal 5 (common/ground for analog signals).
- Use shielded cable to reduce noise, and connect the shield’s drain wire to ground at the VSD end only to avoid ground loops.
- Alternative (4–20 mA) : If using a 4–20 mA signal, connect the current source to terminal 4 (current input) and terminal 5 (common). Set Pr. 73 accordingly (see Step 3).
- Wire Control Inputs for PU/EXT Switching :
- Connect a toggle switch or push-button between terminals STF (forward start) and PC (24 V common) for start/stop control in EXT mode.
- Optionally, connect a switch between terminal MRS (output stop) and PC to enable/disable the VSD output.
- For PU/EXT mode switching, no additional wiring is needed as this is controlled via the operation panel or parameters.
Step 2: Configure PU and EXT Analog Speed Reference Control
Set Operation Mode for PU/EXT Combined Operation :
- Navigate to Pr. 79 (Operation Mode Selection) .
- Set Pr. 79 = 3 (PU and External combined operation mode). In this mode:
- The PU (keypad) controls the frequency reference in PU mode.
- In EXT mode, the frequency reference comes from the external analog input (e.g., terminal 2 or 4) when the AU terminal is active.
- Start/stop commands in EXT mode are controlled by external signals (e.g., STF-PC).
- Switching between PU and EXT modes is done using the [PU/EXT] key on the operation panel.
Assign AU Terminal Function :
- Navigate to Pr. 179 (RL Terminal Function Selection) .
- Set Pr. 179 = 4 to assign the AU (analog input selection) function to the RL terminal (used as the AU terminal).
- When the AU-PC circuit is closed (e.g., via a switch), the VSD uses the analog input (terminal 2 or 4) as the speed reference in EXT mode. When open, the speed reference may default to another source (e.g., PU setting, depending on Pr. 339).
Configure Analog Input for EXT Mode :
- Navigate to Pr. 73 (Analog Input Selection) .
- For a 0–10 V potentiometer, set Pr. 73 = 1 (terminal 2, 0–10 V input).
- For a 4–20 mA signal, set Pr. 73 = 5 (terminal 4, 4–20 mA input).
- Ensure Pr. 73 enables the correct voltage/current input when the AU terminal is active (e.g., Pr. 73 = 5 for 4–20 mA with AU).
Reference Resources:
and Emanual Viewer (Recommended)